FabyaVisionUser Manual
/

Troubleshooting guide

13 min readTroubleshooting

From symptom to cause and solution: Live does not start, no connection can be established, no tag value arrives, no alarm or trend, the script does not run, the on-screen keyboard or remote monitoring does not work. Based on the real error messages.

Where to start

  1. Look at the problem list

    In Studio, F7 Check the project: most address, connection, script and setting errors show up here, before the project is even uploaded to Live.

  2. Check the connection state in Live

    System menu › Connections shows the state of each connection and, when it is disconnected, the reason.

  3. Check the event log

    Script errors, connection losses, and session and setting changes are in the event log (Event view object). Program messages are in the logs folder. Details: Log files.

  4. If you have problems with scheduled tasks

    See the System menu › Tasks… window (below).

Installation and startup

SymptomCauseSolution
Setup reports Setup files are missing or damaged. … and installs nothingThe Data folder is not next to the setup program, or it was copied incompletely or corrupted. The message shows the file name.Copy the complete Data folder again and check it against SHA256SUMS.txt (Installation).
The setup program says FabyaVision requires Microsoft .NET Framework 4.8; it was not found on this computer..NET Framework 4.8 is not installed and its installer is not included in the setup files (Data\Prerequisites is missing).Copy the complete Data folder, or install .NET Framework 4.8 and run the setup again.
Components that are missing on this computer (.NET Framework 4.8 / WebView2 Runtime) can only be installed with administrator rights.Setup ran without administrator rights (/CURRENTUSER).Right-click the setup program and choose Run as administrator.
Microsoft .NET Framework 4.8 could not be installed (exit code N).The .NET installer reported an error (on Windows 7 usually because of missing updates).Check the log named in the message (%TEMP%\FabyaVision_ndp48.log); update Windows and run setup again.
At the end of setup, Microsoft Edge WebView2 Runtime could not be installed on this computer.WebView2 is not installed and the setup program could not install it.Install the WebView2 Runtime with the "Evergreen Standalone Installer". Studio, Live and Convert do not start until it is installed.
Setup could not be completed in the setup windowThe silent installation stopped with an exit code.Use Open setup log to view the %TEMP%\FabyaVision_Setup_<tarih_saat>.log file; read the message under Notes.
FabyaVision Setup is already running.Another setup window is open.Use the setup window that is open, or close it and start the setup again.
At startup the message Microsoft Edge WebView2 Runtime is not installed on this computer. appears and the program closesWebView2 Runtime is missing.Same: install the Evergreen Standalone Installer (x86 / x64) and restart the program. The line WebView2 Runtime yok appears in the log.
The interface could not be started: …WebView2 could not be started.See the details of WebView2 baslatilamadi in the log; reinstall the WebView2 Runtime.
The Select project screen appears when Live startsNo project is given on the command line and Start automatically with the last project is off (or there is no last project file).Select the project or turn on automatic start (Live overview).
There is no project in this folder.There is no Live file (.fvl) in the project folder.In Studio, transfer the project with Upload project to Live… or use Open from file….
Project folder not found.The folder has been deleted or disconnected from the network.Select an existing folder with Change folder….
The card is red: Unreadable — Project file is damaged: invalid JSON format (line N).The project file is damaged or was copied incompletely.Restore from the backup (the Yedek folder) or upload the project again from Studio.
The project could not be opened (path): …The file could not be read (corrupt, locked, or no access). A setup error may also occur while the screen / tag count is being loaded.Fix the cause given in the message; look for the line Proje okunamadi in the logs folder. In Recover mode the selection screen opens again.
The screen reloaded by itself while runningThe WebView2 render process crashed (RenderProcessExited).Live reloads the screen and recovers from where it stopped (drivers and tags restart). If this happens often, keep the log (WebView2 sureci coktu: RenderProcessExited). If Live closes suddenly, look for the BrowserProcessExited line in the log.

License

SymptomCauseSolution
The license page appears before the program opensThe required license is not on this computer, belongs to another computer, has expired, or the USB drive is not connected. The page states the reason.Send the machine code to FabyaVision and drop the .fvk files you receive onto the page (License and activation).
Red strip at the bottom: License revoked by FabyaVision — …According to the online check, the license in use has been revoked or moved to another computer. The program keeps running.Contact FabyaVision; if you close the program, it will not start with this license (Online license check).
Red strip at the bottom: License could not be verified — contact FabyaVision.The license check during operation failed. The program keeps running; Live does not open new sessions for browser monitoring, and Studio does not perform Start Runtime or uploads to Live.Keep the LISANS: line from the program log and contact FabyaVision.
No OPC UA server license (FV-OPC): the server was not started. · No Notification Center license (FV-NTF): notifications are not sent. · No performance report license (FV-PRF): plans are not running.There is no license file for a feature that is on in the project. Live and the plant keep running.Add the license file and reopen Live (Option licenses).
The trial version does not open: Internet connection requiredThe trial version could not be activated online at first start.Connect to the internet and click Retry, or request an offline activation file (Trial version).

Communication and tag values

SymptomCauseSolution
In the System menu, the connection shows no connectionThe device cannot be reached or the device refuses the connection. The red text below the connection gives the reason.See the Connection and driver messages table.
Connection no driverThe driver of the connection could not be created or is not supported.Check the driver type and the parameters; the log may contain a Surucu olusturulamadi (…) line.
The connection shows no connection but there is no red messageThe first connection attempt is in progress (the connecting state is not shown); the device does not respond during the timeout.Wait a few seconds; the message is written at the end of the attempt. If it does not appear, check the IP, the network and the firewall; try increasing the Timeout value.
The connection has an Enter password button and does not connectThe OPC UA / MQTT / OPC DA connection requires a user name and password; no password has been entered (… password not entered).From the System menu, Enter password (requires the settings authorization). The password is not written to the project file; it is stored on this computer.
No value / zero in the objectThe tag could not be read (no connection, address error) or the first value has not arrived yet.See the quality codes below and the tag read errors table.
The value is present but wrongThe tag type / address does not match the one in the PLC; scaling; byte order.Correct the Data type and the address according to the actual type in the PLC (Tag addresses).
Value cannot be written: Operation failedOut-of-limits value, connection state tag, authorization.See the message table in the operator guide.

Quality codes

In scripts, tag quality is numeric: 192 good · 84 value outside the tag limits (usable) · 8 no connection · 4 undefined · 0 bad. In C, the status code: 0x0001 no connection, 0x0080 value not read yet, 0x0200 address error, 0x0400 no tag.

Alarms, trends and other functions

SymptomPossible causeSolution
No alarms are generatedIn the Startup sequence, Alarm system is off; the trigger tag of the alarm is not selected (… not selected; the alarm never occurs); the trigger tag cannot be read.Check the startup sequence and the alarm definition; view the value of the tag in Live. See Alarm definition.
The alarm line is not visible or the alarm cannot be acknowledgedShow alarm line is off; there is no active alarm; the user does not have the alarm acknowledgment authorization.Live settings › General › View; log on with an authorized user.
Trend is emptyIn the Startup sequence, Data logging is off (no new records are written); no tag is selected in the archive; a text tag cannot be drawn as a trend; there is no data in the time range.Check the data archive definition and the start sequence (Historical data). If the archive cannot write to SQL, the program log contains the line Arsiv SQL (…): baglanti / yazma hatasi; the rows wait in the disk buffer.
The recipe button says Recipes are turned off in Live settings › Startup sequenceThe recipe service is turned off.In the Startup sequence, turn on Recipes.
Reports are not recorded automaticallyReport recorder is off or no trigger tag has been selected.Check the startup sequence and the Trigger and record setting of the report.
Alarm e-mail or SMS is not sentNotifications are off; the rule does not match the alarm; the channel setting or password is missing; Live is closed.In Live, read the status and delivery log in the Notification center… window and send a test (Notification Center window).
An external OPC UA client cannot connectPort, security mode, certificate trust or firewall.Common connection errors
Performance report shows no dataThe tag is not in a data archive.Add the tag to an archive (Performance reports).
A screen does not appear in the system menuThe list shows only the start screen and the favorite screens.Make the screen a favorite or add a navigation button (Favorite pages).
Screen does not open, The … screen requires the … authorizationThe user in the session has no authorization / no session.Log on with an authorized user. If the screen is a draft (marked as draft), it is never opened in Live.

Scripts and scheduled tasks

Script errors, the time limit, permissions and all messages are covered in Script and task problems. If a task does not run, first look at the window below: the Inactive, no script selected or Not run yet state shows the cause; Startup sequence must also be switched on in the Scheduled tasks.

System menu › Tasks…: the trigger of each task, its last run, its result, its next scheduled time and its run count.123
System menu › Tasks…: the trigger of each task, its last run, its result, its next scheduled time and its run count.
  1. Summary — the number of tasks, enabled tasks and faulty tasks; the current time.
  2. Result — OK, Error, Skipped, Inactive … The error message appears below.
  3. Next — next scheduled run time.

The Tasks… window refreshes every second. The Result column shows OK, Error, Skipped (e.g. triggered again while the previous call was still running), Running, Inactive, Completed (one-time task) or Not run yet; the error and skip message is written below the row. The Next column shows the next scheduled time for time-triggered tasks; for the others it shows cyclic, by tag, at startup or at shutdown. The task state is stored on this station.

On-screen keyboard, camera, and remote monitoring

SymptomCauseSolution
The on-screen keyboard does not openIn the System menu, On-screen keyboard is Inactive; the field is read-only / disabled; monitoring from a browser (the keyboard never opens there).Set the switch to Active (On-screen keyboard).
The camera object says No camera serverThe main program could not start the camera server (the local listener could not be opened).In the logs folder, look for the line Kamera sunucusu baslatilamadi. Camera states: Off, Queued, Connecting, Connected, Error. See IP camera.
The screen does not open from the browser (timeout)No Windows Firewall permission; the Live PC is not on the network; wrong port.In Live, system menu › Remote monitoring… › Add firewall permission. Copy the address from the same window.
403 Access from this address is not allowed.The client's address does not match the access rule.Add the Last rejected address shown in the Live window to Access Networks.
Login fails: User name or password is incorrect.The browser user has no password / the password is wrong.In Studio, enter the password again under Browser users.
Too many failed attempts. Try again in N seconds.5 failed logins from the same address.Wait (60 seconds).
Port number … is being used by another program; browser monitoring could not be started.Port conflict.In Studio, change Remote monitoring › Port.
In the viewer, Live PC is not responding — data is not up to dateThe server responds, but the Live main engine has not been broadcasting for 15 seconds.Check the Live PC (load, freezing).
The TV does not open at allNo suitable second display is available (a display other than Live's display, the monitors covered by the multi-display setup and the monitors used by Separate page on each monitor is required).In the Live › Remote monitoring window, check the status of Second screen (TV) (Multiple displays and TV).
This user is connected from another computer (…). The same user can sign in from only one computer at a time.The same browser user is logged on at another computer.On the other computer, press Logout, or close the browser and wait 15 seconds. Create a separate user for each person (Remote monitoring).
In the browser, Remote monitoring: control disabledThe user has no authorization group, or Remote control is off.In Studio, enable Remote monitoring › General › Remote control, select a group in Browser users and load the project to Live (Remote control).
In the browser, This action is only possible on the Live computerAn action that is not possible in remote control (closing the program, the Live session, station settings) or a database / file / program operation of a script.Perform the action from the Live computer.
Cannot write to the database (…) in the event logSQL Server is not running, the server / database name is wrong, or Live's Windows account has no permission in SQL Server.The records wait in the local file. Correct the server and the permission (Project database).

Before requesting support

If you cannot solve the problem, prepare the list Information to collect for support in the topic Log files: the logs folders, the project file, the event log files, the version information and a screenshot of the problem.

Related topics

FabyaVision 1.2.1 User Manual · 2 November 2026© Fabyatek Yazılım Bilişim Teknolojileri Ltd. Şti.